For those of you who have heat pumps, especially dual systems, what temp is your supplemental heating set to? Mine was set by the HVAC guys to 26 to switch to the propane furnace. The temps here the last few days have been running around high 20s-low 30s from after sunset through late morning-early afternoon. Just above my switchover.

I have noticed my unit just running and running, and going into defrost mode (I know that's a good thing) like crazy. While electricity is dirt cheap here, I'm wondering if it wouldn't be more efficient for me to move the switchover for propane to 29-30deg. As Mike Irwin likes to point out  ;) , heat pump heat can seem cold. Mine, at these temps, puts around 80 deg out the registers, and seems to struggle with that (compared to ~90deg if it's in the 40s, or ~110deg with the gas furnace any old time). So while it's keeping the temps at 69 [Kevin Malone], it's always a "cool" 69 unless I have the wood stove going. Big difference in feeling from waking up on a 15deg morning when the propane furnace has kicked in at 0500 and heated the house for me.

All the charts I see on the interwebz seem to have the temps I'm currently experiencing (with 30deg the "average") as where the lines cross for efficiency vs inefficiency. So I'm smack in the middle of "six of one, half a dozen of the other" right now.  :laugh:
Title: Re: Heat Pump Question
Post by: MillCreek on November 29, 2019, 01:51:20 PM
I think mine is set to switch over to the auxiliary electric heating coils at 26 degrees.  When my system makes that switch, the electric power meter spins like a dervish and I really see it in that month's power bill.
Title: Re: Heat Pump Question
Post by: Ben on November 29, 2019, 01:57:51 PM
I think mine is set to switch over to the auxiliary electric heating coils at 26 degrees.  When my system makes that switch, the electric power meter spins like a dervish and I really see it in that month's power bill.

I'm trying to figure out if my unit has electric coils as well, and if those are used during defrost (when basically the AC is running instead of heat). Because I was curious about the "midnight to six" run time so have been tracking on the Idaho Power site, where I can see my hourly usage, and that timeframe/temp when there would be a lot of defrosting is jumping up in KW like crazy. The furnace should only be using like half the juice of the heat pump, which has me wondering if the HP is using coils instead of propane during defrost cycles.
Title: Re: Heat Pump Question
Post by: K Frame on November 29, 2019, 05:56:33 PM
If you have a propane secondary it should kick in when defrost mode engages.

Essentially defrost mode for a heat pump is turning on the air conditioning.  It pulls heat out of the house and sends it through the exterior coils to defrost them.

The secondary kicks in to negate the loss of heat. I doubt that you have two secondary heaters - propane and electric.

My heat pump hasn't run in November.

My pellet stove has.

Sent from my SM-G960U using Tapatalk
Title: Re: Heat Pump Question
Post by: K Frame on December 03, 2019, 07:47:29 AM
So what's the deal, Ben? Have you figured out how your system is set up?

Do you have both electric coils AND the propane cheater heater? I've done some digging around and, while not a common set up, it has been done, especially if the propane is set up to be "stage 2" heating, which it sounds as if yours may be.



And, speaking of heat pumps... Mine hardly ran at all in November. I have it set at 60 degrees to provide a back up to the pellet stove. It ran a bit when I was away for Thanksgiving, but when I got home on Sunday, the house was right at 60 degrees.

I kicked the pellet stove on to level 3, and within an hour it was 75 in the living room and heat was rushing upstairs. By the time I went to bed I had cut the stove back to level 1, it was 78 in the living room, 72 in the front hall, and 75 upstairs.

Good God I love my pellet stove.
Title: Re: Heat Pump Question
Post by: Ben on December 03, 2019, 08:45:28 AM
I still have no idea. I wouldn't even know how to check for heating strips. I'm leaning towards maybe not, as I've been watching the system closely during these "borderline" temperatures. I've noticed - this morning at 30deg for example - that the system will sometimes switch to propane (even though it's set to do so at 26deg), I guess if the heat pump has been running too long or doing too many defrost cycles and not gaining temperature?

It's supposed to be some kind of smart system. I also noticed the other day, it was 67 inside, again around freezing outside, and I was feeling a bit chilled, so I knocked the temp up to 73. It went straight to aux heat, I guess already figuring that would be too great a burden on the heat pump at that temp?
Title: Re: Heat Pump Question
Post by: Ron on December 03, 2019, 08:59:01 AM
I still have no idea. I wouldn't even know how to check for heating strips. I'm leaning towards maybe not, as I've been watching the system closely during these "borderline" temperatures. I've noticed - this morning at 30deg for example - that the system will sometimes switch to propane (even though it's set to do so at 26deg), I guess if the heat pump has been running too long or doing too many defrost cycles and not gaining temperature?

It's supposed to be some kind of smart system. I also noticed the other day, it was 67 inside, again around freezing outside, and I was feeling a bit chilled, so I knocked the temp up to 73. It went straight to aux heat, I guess already figuring that would be too great a burden on the heat pump at that temp?
Being a "smart" system the thermostat or system operates as a two stage system most likely. On a normal call for heat (one or two degrees under the set point) stage one is energized. If the temperature drops too low below set point stage two/aux heat/emergency heat is energized.

I doubt you have electric and gas auxillary heat. If you don't have dedicated breakers in your panel for electric heat you probably don't have electric strips.

My knowledge of heat pumps is limited but as mentioned above in another post, if the coil is in defrost or not generating enough heat stage two, aux/emerg heat will be energized.
Title: Re: Heat Pump Question
Post by: K Frame on December 03, 2019, 09:33:28 AM
"I doubt you have electric and gas auxillary heat. If you don't have dedicated breakers in your panel for electric heat you probably don't have electric strips."

When I bought my house in 1993 I had a 6 SEER Bryant system with electric coil emergency/backup heat.

It was replaced in 1995 with a 12 SEER Trane system with electric coil emergency/backup heat.

In neither case were there separate breakers in my electrical box for the emergency/backup coils -- those breakers were/are on the air handler unit itself with master breakers on the panel to control the entire heat pump/air handler system.
Title: Re: Heat Pump Question
Post by: Ron on December 03, 2019, 09:56:37 AM
"I doubt you have electric and gas auxillary heat. If you don't have dedicated breakers in your panel for electric heat you probably don't have electric strips."

When I bought my house in 1993 I had a 6 SEER Bryant system with electric coil emergency/backup heat.

It was replaced in 1995 with a 12 SEER Trane system with electric coil emergency/backup heat.

In neither case were there separate breakers in my electrical box for the emergency/backup coils -- those breakers were/are on the air handler unit itself with master breakers on the panel to control the entire heat pump/air handler system.
interesting, i guess in the commercial world the current draws are such the heat coils warrent their own circuit. As mentioned my residential heat pump knowledge is limited.

Have you had a system that employed both gas heat and electric heat as its auxillary? Seems mighty redundent.
Title: Re: Heat Pump Question
Post by: Nick1911 on December 03, 2019, 09:59:42 AM
Heat pumps move less heat and have a lower COP as the difference between inside and outside temperature increases.

Your balance point, the outside temperature at which the heat pump is able to provide just enough heat to keep the building at the setpoint by running nonstop, is particular to each building, as each building has its own unique heat loss/gain characteristics.

Economically, this balance point might be somewhere different.  In the KC metro area, only very high end heatpumps have a chance of competing with natural gas furnaces.  Natural gas is just very inexpensive.

We fairly easily find that out for your setup.  Post the model numbers of your equipment, your per KWhr electric cost, and your local propane cost.  =)
Title: Re: Heat Pump Question
Post by: K Frame on December 03, 2019, 10:57:57 AM
'Have you had a system that employed both gas heat and electric heat as its auxillary? Seems mighty redundent.'

No, but I did find a little bit of information on such a set up when poking around online. Or at least what appeared to be some information on a set up like that.

The way it was described was that the propane system wouldn't be "armed" until the exterior temperature dropped to a certain point (I guess sort of like an outdoor reset concept).

Until that happened, the electric unit would provide the supplemental heat. Once that outside temp was reached, the coils would be taken out of the equation.

I agree. That seems as if it's ridiculously redundant
Title: Re: Heat Pump Question
Post by: K Frame on December 03, 2019, 11:04:47 AM
"Heat pumps move less heat and have a lower COP as the difference between inside and outside temperature increases."

Not sure that I understand this...

I thought COP was purely the amount of usable heat that a unit could deliver at a given outdoor temperature, and that the temperature inside the house had nothing to do with it other than requiring to unit to run shorter or longer depending on the call to temperature.
Title: Re: Heat Pump Question
Post by: Nick1911 on December 03, 2019, 11:45:38 AM
COP is an efficiency metric.  It does not indicate how much heat is moved, only how efficiently that heat is moved.  It's a ratio.  For example, if a unit is operating at a COP of 3, you are getting three units of heat indoors for one unit of input energy.  It's a dimensionless ratio, so you can apply it however you want, 3 watts of heat moved for 1 watt input, BTU's, whatever.

The actual amount of heat moved is a separate thing.  It's dictated by the difference in indoor and outdoor temperature, although for most purposes, it's assumed that the indoor temperature is constant.

The amount of heat a given heat pump can move drops as the indoor/outdoor temperature split increases.  A the same time, the buildings heat loss increases.  Where the two cross each other is the balance point.

To try to make this a little more concrete, let me use some actual information from a real heatpump. (GSZ14040)

Assuming you're trying to keep the house at 70F:
If it's 50F outside, this heat pump moves a lot of heat, 29,920 BTU/hr.  It also does this very efficiently, consuming only 2.31KW, a COP of 3.80.
If it's 30F outside, this heat pump moves a some heat, 19,620 BTU/hr.  It also does this somewhat efficiently, consuming 2.08KW, a COP of 2.77.
If it's 0F outside, this heat pump moves a little heat, 9,290 BTU/hr.  It's not very efficient, consuming 1.74KW, a COP of 1.57.  (still better then heat strips)

Heat loss from the building works the other direction.  A building that needs 20,000 BTU's to stay at 70F inside when it's 50F outside might need 70,000 BTU's when the outside temperature drops to 0F.
Title: Re: Heat Pump Question
Post by: Ben on December 03, 2019, 11:47:27 AM

We fairly easily find that out for your setup.  Post the model numbers of your equipment, your per KWhr electric cost, and your local propane cost.  =)

Coincidentally, the propane guy was by yesterday, so current costs are:
Propane: $1.73/gal
Electricity is on a tiered plan and I always make it well into the 2nd tier, but lets average at $0.085.

I can't read this guy's handwriting well, but I'll post the invoice and also a photo from the tag on one part of the unit (don't know if it's AC or furnace). The whole thing is Amana (which I guess is also Goodman?):

(https://live.staticflickr.com/65535/49163670983_fa5c7b2019_z.jpg)
(https://live.staticflickr.com/65535/49164126386_31e6731526_z.jpg)
Title: Re: Heat Pump Question
Post by: Ron on December 03, 2019, 12:01:26 PM
Pretty unlikely you have electric heat on top of a newer two stage gas furnace.

Not to mention he didn't write anything down regarding electric heat.
Title: Re: Heat Pump Question
Post by: K Frame on December 03, 2019, 12:15:31 PM
COP is an efficiency metric.  It does not indicate how much heat is moved, only how efficiently that heat is moved.  It's a ratio.  For example, if a unit is operating at a COP of 3, you are getting three units of heat indoors for one unit of input energy.  It's a dimensionless ratio, so you can apply it however you want, 3 watts of heat moved for 1 watt input, BTU's, whatever.

The actual amount of heat moved is a separate thing.  It's dictated by the difference in indoor and outdoor temperature, although for most purposes, it's assumed that the indoor temperature is constant.

The amount of heat a given heat pump can move drops as the indoor/outdoor temperature split increases.  A the same time, the buildings heat loss increases.  Where the two cross each other is the balance point.

To try to make this a little more concrete, let me use some actual information from a real heatpump. (GSZ14040)

Assuming you're trying to keep the house at 70F:
If it's 50F outside, this heat pump moves a lot of heat, 29,920 BTU/hr.  It also does this very efficiently, consuming only 2.31KW, a COP of 3.80.
If it's 30F outside, this heat pump moves a some heat, 19,620 BTU/hr.  It also does this somewhat efficiently, consuming 2.08KW, a COP of 2.77.
If it's 0F outside, this heat pump moves a little heat, 9,290 BTU/hr.  It's not very efficient, consuming 1.74KW, a COP of 1.57.  (still better then heat strips)

Heat loss from the building works the other direction.  A building that needs 20,000 BTU's to stay at 70F inside when it's 50F outside might need 70,000 BTU's when the outside temperature drops to 0F.


OK, that I understand, and that lines up with what I was saying earlier.

What I'm trying to factor in, though, is this statement: "Heat pumps move less heat and have a lower COP as the difference between inside and outside temperature increases."

When I initially read it, it seemed to say that COP was a factor of the difference between the two temperatures, which would mean that no matter what the outdoor temperature, the COP would be the same if there was a differential of 40 degrees (30 outside, 70 inside or 20 outside 60 inside).
Title: Re: Heat Pump Question
Post by: Nick1911 on December 03, 2019, 12:31:26 PM
Good.  Here’s the technical manual for that heat pump: https://www.alpinehomeair.com/related/Amana%20ASZ16%20Spec%20Sheets.pdf
Here’s the relevant section
(https://i.imgur.com/oKcnzQW.png)
The furnace is very efficient, with a rated AFUE of 96%.

There’s a couple ways we can drive at this, but to most clearly lay it out lets ask the question: How much money would it cost to get 100,000 BTU’s from each heat source?

Starting with the propane furnace.  1 gallon of propane contains 91,000 BTU’s of energy.  To get 100,000 btu’s in your building:

100,000 BTU into building / (96%) = 104,100 BTUs burnt.  (1 gallon propane / 91,000 BTUs) = 1.145 gallons.  Total cost for 100,000 btus into the building: $1.98.

For the heatpump, this will change depending on the outdoor temperature.

Lets look at the worst case scenario: electric resistance heat (space heaters, heat strips, baseboard heaters)

To get 100,000BTU’s, you would need to consume 29,291 watts, 29.29KW.  A cost of $2.49.

Here’s how the COP works with a heat pump.  It’s an efficiency ratio.  For a heatpump to deliver 100,000 BTU’s, we still need 29.29KW of heat, but we can get some of that from outside the house with the heat pump.  So, we don’t have to put in a full 29.29 KW.  Using the product documentation, here’s where we get with cost of operation, assuming a 70F indoor temperature:
Outdoor TempCOPCost per 100,000 BTUs
65 4.66 $0.53
55 4.30 $0.58
47 3.95 $0.63
45 3.86 $0.64
40 3.65 $0.68
35 3.43 $0.73
30 3.27 $0.76
25 3.08 $0.81
20 2.89 $0.86
17 2.76 $0.90
15 2.68 $0.93
10 2.45 $1.02
5 2.22 $1.12
0 1.97 $1.26
-5 1.72 $1.45
-10 1.44 $1.73
Therefore, economically, with the cost of energy in your area, your heatpump is always cheaper to operate then propane.
It’s in your best interest to run the heat pump as much as you can, until it becomes cold enough that the heat pump can’t keep up.  Only run propane when you are forced to.

However, propane is cheaper then electric resistance heat.  Run propane before you run space heaters.
Title: Re: Heat Pump Question
Post by: Nick1911 on December 03, 2019, 12:37:23 PM
When I initially read it, it seemed to say that COP was a factor of the difference between the two temperatures, which would mean that no matter what the outdoor temperature, the COP would be the same if there was a differential of 40 degrees (30 outside, 70 inside or 20 outside 60 inside).

This is correct.  It's usually glossed over because people usually want their indoor spaces at a constant temperature.  =)

The efficiency of heat pumps is governed by the carnot cycle.  What matters here is the difference in temperature between the two sides.

The SEER and EER of an air conditioner/heat pumps are limited by the laws of thermodynamics. The refrigeration process with the maximum possible efficiency is the Carnot cycle. The COP of an air conditioner using the Carnot cycle is:

(https://wikimedia.org/api/rest_v1/media/math/render/svg/3cbea5c0a70672962fa508cae8c23c19fbd97e79)

where TC is the indoor temperature and TH is the outdoor temperature. Both temperatures must be measured using a thermodynamic temperature scale based at absolute zero such as Kelvin or Rankine
Title: Re: Heat Pump Question
Post by: K Frame on December 03, 2019, 01:10:30 PM
"This is correct.  It's usually glossed over because people usually want their indoor spaces at a constant temperature."

Those privileged bastards!

OK... Thinking about this some more, I think I now get what you're saying, and the more I think about it, the more sense it makes...

Correct me if I'm wrong, but...

The COP differential between the two temperature sides comes down (is affected? determined? influenced?) to the outside is limited to what heat it can pull from the outside air, but the inside is limited by how much of that heat can be moved into the building from the interior coil?

I tried reading the Wikipedia entry on the Carnot cycle... yikes.
Title: Re: Heat Pump Question
Post by: K Frame on December 03, 2019, 01:13:14 PM
"However, propane is cheaper then electric resistance heat.  Run propane before you run space heaters."

And both propane and space heaters are warmer than a freaking heat pump.

Run a pellet stove!

 :rofl:
Title: Re: Heat Pump Question
Post by: Ben on December 03, 2019, 01:24:47 PM
Thanks Nick - that was very helpful, especially regarding the space heaters.

One of the things I've been doing is running the wood stove, which nicely warms most of the house. Except, irritatingly, my office, where I spend a good part of my time when indoors, and the master bedroom. When running the wood stove,  I supplement those two rooms with radiant oil heaters for part of the day. Sounds like maybe it's cheaper to run the central propane for a short period instead?

While I appreciate that with my electric costs, the heat pump is much cheaper to operate, I'm still with Mike on the "cold-feeling" heat. When it's in that high 20s - low 30s range outside, I often get a little chill when I feel the "heat" from the heat pump blowing out of the registers.  :laugh:
Title: Re: Heat Pump Question
Post by: Ron on December 03, 2019, 01:34:36 PM
Have tried turning your blower on while running the wood stove?

Circulate the air in the house to even the temp in the rooms out a little.
Title: Re: Heat Pump Question
Post by: K Frame on December 03, 2019, 01:40:42 PM
The fan on my heat pump system is constantly on. It runs 24x7x365 as much to filter the air as to equalize temperatures throughout the house.

You can also put a box fan in your bedroom or office. Set it in the door opening so that it is blowing OUT of the bedroom.

It will move cold air out of the bedroom and pull in warmer air from the hallway. Because of the relative densities, it's easier to move cold air rather than warm air.
Title: Re: Heat Pump Question
Post by: Ben on December 03, 2019, 02:10:54 PM
Have tried turning your blower on while running the wood stove?

Circulate the air in the house to even the temp in the rooms out a little.

Yeah, for an expensive stove though, that blower is freakin' loud if I'm sitting in the living room and watching tv or reading. Instead, once the stove is pumping heat out really well, I turn on the ceiling fan above it, which distributes the warm air well. The problem is that the office and master bedroom, kinda connected to each other, are past a small hall that somehow is really good about blocking heat distribution.

My heat pump fan is set to auto. I might try setting it to full time on for a while to see if it makes a difference.
Title: Re: Heat Pump Question
Post by: Ron on December 03, 2019, 02:30:18 PM

My heat pump fan is set to auto. I might try setting it to full time on for a while to see if it makes a difference.

That's what i meant, furnace blower
Title: Re: Heat Pump Question
Post by: K Frame on December 03, 2019, 02:30:48 PM
"kinda connected to each other, are past a small hall that somehow is really good about blocking heat distribution."

Box fan. Play around with where it's located. You'll find the sweet spot.
Title: Re: Heat Pump Question
Post by: K Frame on December 03, 2019, 02:34:53 PM
"I might try setting it to full time on for a while to see if it makes a difference."

And what, pray tell, is the purpose of a fan connected to a duct work system that is designed to distribute conditioned air?

It's designed to keep the air in the house moving around to increase comfort... It doesn't matter exactly how that air is conditioned... if the fan is on, it will move it through the duct work.

Does it move air when it's off?

Jesus wept, Dude!  :facepalm:
Title: Re: Heat Pump Question
Post by: Ben on December 03, 2019, 02:44:36 PM
Well, there appear to be pros and cons:

https://trusthomesense.com/blog/pros-cons-continuously-running-hvac-fan/

I just checked, and my thermostat has the "circulate" function. I might try that. Having the fan on all the time seems like it will give me the same feeling as when the heat pump is on - while it may be circulating warmish air, the blowing air may feel cool to me. If I can set it to circulate for a set time every hour, that might be a good compromise.

I have dedicated air filtration units in the house, so  I don't need to run an HVAC fan for air cleaning.
Title: Re: Heat Pump Question
Post by: charby on December 03, 2019, 03:22:02 PM
Well, there appear to be pros and cons:

https://trusthomesense.com/blog/pros-cons-continuously-running-hvac-fan/

I just checked, and my thermostat has the "circulate" function. I might try that. Having the fan on all the time seems like it will give me the same feeling as when the heat pump is on - while it may be circulating warmish air, the blowing air may feel cool to me. If I can set it to circulate for a set time every hour, that might be a good compromise.

I have dedicated air filtration units in the house, so  I don't need to run an HVAC fan for air cleaning.

No, it will help balance out the warm and cold areas of the house. I flip my furnace fan to continuously on when its below 10 degrees or above 95F. I find it more uncomfortable when the air isn't moving between the furnace or air-conditioning cycling during extreme weather events.

Also if your wood stove doesn't get fresh air from outside for the firebox, it has to draw air from somewhere. Cold air is drawn through all the micro leaks around doors and windows, making the farthest rooms feeling even colder.  
Title: Re: Heat Pump Question
Post by: K Frame on December 03, 2019, 06:09:02 PM
On circulate your fan should only run at quarter speed or so, not the same speed as when the unit is in heating or cooling mode.

You shouldn't notice circulation mode at all.

Sent from my SM-G960U using Tapatalk
Title: Re: Heat Pump Question
Post by: Ben on December 03, 2019, 07:08:03 PM
On circulate your fan should only run at quarter speed or so, not the same speed as when the unit is in heating or cooling mode.

You shouldn't notice circulation mode at all.

Sent from my SM-G960U using Tapatalk

So far I haven't. It's up to the mid 30s right now, so I didn't have the stove on today. When it's just the central running, it actually distributes the heat pretty evenly - better than any HVAC I've had in the past. The test will be when I do the "heat by wood stove only" thing. I think I'll be a fan of "circulate mode" though.
Title: Re: Heat Pump Question
Post by: K Frame on December 04, 2019, 07:43:47 AM
"https://trusthomesense.com/blog/pros-cons-continuously-running-hvac-fan/"

Wow... I knew leaving the fan on my air handler run 24x7 used electricity, but I didn't realize it had the potential to use quite that much electricity.

I'm thinking I'm going to try a bit of an experiment. I'm going to turn the fan to the auto position for a month, and monitor my electrical usage and the temperature distribution and differentials.

Title: Re: Heat Pump Question
Post by: Ben on December 04, 2019, 08:21:55 AM
"https://trusthomesense.com/blog/pros-cons-continuously-running-hvac-fan/"

Wow... I knew leaving the fan on my air handler run 24x7 used electricity, but I didn't realize it had the potential to use quite that much electricity.

That threw me too. It actually sounds abnormally high. Or else they used numbers from a state with high electricity costs. My entire bill last month was $90, so their number would be more than a 50% increase just running the fan. Potentially another plus for "circulate" I guess.

Title: Re: Heat Pump Question
Post by: K Frame on December 04, 2019, 09:17:24 AM
My bill for November was $88.85 with a usage of 605 KwHR. That would have been higher, probably closer to 900-1000 KwHr, had I been using the heat pump.

I'm on budget billing, which smooths out the bill to the same amount every month, which right now is $108.99. I should be able to cut that quite a bit by not using the heat pump.


My lowest bill over the last year was 508 KwHR in April, but I was away for 2 weeks of that billing period. It would have been even lower had I turned my water heater either to vacation mode or completely off. I didn't realize I was going to be away that long, so I didn't.

This weekend I'm going to go through the house and kill all of the 'phantom' power draws that I can; things like the TV in the basement, the clock radios in rooms I don't use that much, etc., the computer in my office, which I only use on weekends, etc. Between those and the fan on the air handler, I'm thinking I might be able to drop another 50-100 KwHr off my usage.

That's going to be a 1 or 2 month experiment. We'll see how it works out.
Title: Re: Heat Pump Question
Post by: Ben on December 04, 2019, 09:40:54 AM
My bill for November was $88.85 with a usage of 605 KwHR. That would have been higher, probably closer to 900-1000 KwHr, had I been using the heat pump.


I was a bit over 1000kWh. It was actually slightly more usage than in August, which was peak AC season here, and when I had guests additionally using the split AC system upstairs. However besides the house, I've also got heat to the wellhouse running on a thermostat timer, which ends up using a good bit of juice. And these portable oil heaters use a good bit more electricity than a fan does in the Summer. :)

I had made some notes on days I used the wood stove most of the day, and looking at those days on the power company website, they were pretty significant usage reductions.
Title: Re: Heat Pump Question
Post by: Jim147 on December 05, 2019, 09:09:13 PM
A change over point around here from 26-28 degrees is very common. Using the wood stove with the fan may feel cool in some rooms but so does a heatpump to me. Nick and Ron always have some good answers on these topics. And Mike seems to know about everything. Haha.
Title: Re: Heat Pump Question
Post by: K Frame on December 06, 2019, 07:50:55 AM
"And Mike seems to know about everything. Haha."

Bow before my VFUK (vast fund of useless knowledge), peasant!
Title: Re: Heat Pump Question
Post by: Jim147 on December 06, 2019, 06:17:23 PM
Love you Mike
Title: Re: Heat Pump Question
Post by: K Frame on December 06, 2019, 10:20:19 PM
Keep it in your pants...

Sent from my SM-G960U using Tapatalk