We've got a Honeywell TH9421C1004 VisionPro IAQ thermostat that currently has a blank screen and a constantly blinking red LED in the upper right corner of the faceplate.  I can't find anything ANYWHERE that states definitely what that light means. There's nothing about it in the thermostat's manual at all, and nothing about it in the heat pump's manual either.

Yesterday we had a long power outage, and after the power came on the screen was much dimmer than usual, and then sometime this afternoon it went away completely and the red light started blinking. It's a wired unit, and I can't find any batteries except what appears to be a coin battery in near-inaccessible location (I could probably get to it if I had to, but it appears they didn't want it to be user-serviceable).

Any of you HVAC guys have any idea what's going on? The heat pump is a Trane 4TWR5, if that helps.

This is kind of what it looks like (I edited it with gimp because I didn't want to get the tripod out to catch the blinking light):




The price of freedom is eternal vigilance. - Thomas Jefferson

Necessity is the plea for every infringement of human freedom. It is the argument of tyrants; it is the creed of slaves. - William Pitt the Younger

Perfectly symmetrical violence never solved anything. - Professor Hubert J. Farnsworth

230RN

  • saw it coming.
  • friend
  • Senior Member
  • ***
  • Posts: 18,870
  • ...shall not be allowed.
Re: Honeywell Thermostat issue - blinking red light of obscurity
« Reply #1 on: September 15, 2017, 11:21:05 PM »
Try unplugging the house and then plugging it back in again.

RoadKingLarry

  • friends
  • Senior Member
  • ***
  • Posts: 21,841
Re: Honeywell Thermostat issue - blinking red light of obscurity
« Reply #2 on: September 15, 2017, 11:22:54 PM »
Honeywell, Rockwell...

Close enough

https://www.youtube.com/watch?v=RXJKdh1KZ0w
If ye love wealth better than liberty, the tranquility of servitude better than the animating contest of freedom, go home from us in peace. We ask not your counsels or your arms. Crouch down and lick the hands which feed you. May your chains set lightly upon you, and may posterity forget that you were our countrymen.

Samuel Adams

TommyGunn

  • friend
  • Senior Member
  • ***
  • Posts: 7,956
  • Stuck in full auto since birth.
Re: Honeywell Thermostat issue - blinking red light of obscurity
« Reply #3 on: September 15, 2017, 11:26:34 PM »
Honeywell, Rockwell...

Close enough

https://www.youtube.com/watch?v=RXJKdh1KZ0w

James Doohan was soooooooooo much better at that... [tinfoil] :laugh: ;/..
MOLON LABE   "Through ignorance of what is good and what is bad, the life of men is greatly perplexed." ~~ Cicero

Nick1911

  • Administrator
  • Senior Member
  • *****
  • Posts: 8,487
Re: Honeywell Thermostat issue - blinking red light of obscurity
« Reply #4 on: September 15, 2017, 11:28:06 PM »
Probably an emergency heat indicator.

From a (different  :lol: ) Honeywell manual:

Heat Pump Emergency Heat LED Indication
(Requires 24 Vac Common Connection)
The thermostat uses a red LED indicator that lights when the thermostat is in the Emergency Heat mode.  The LED is located in the upper right corner of the thermostat.  It is visible only when on.  When the thermost at is in the Em. Heat system mode, the L terminal is continuously energized and the LED is on.

Are you in emergency heat mode?

Regolith

  • friend
  • Senior Member
  • ***
  • Posts: 6,171
Re: Honeywell Thermostat issue - blinking red light of obscurity
« Reply #5 on: September 15, 2017, 11:35:17 PM »
Are you in emergency heat mode?

Nope. Though it's a bit hard to tell because the screen is off.

It was in cool mode prior to the screen blanking. If I pull it off the wall and put it back on, everything comes back up the way it as for a few minutes (still in cool mode), then the screen blanks and the light starts flashing.

The heat pump itself isn't doing anything.
The price of freedom is eternal vigilance. - Thomas Jefferson

Necessity is the plea for every infringement of human freedom. It is the argument of tyrants; it is the creed of slaves. - William Pitt the Younger

Perfectly symmetrical violence never solved anything. - Professor Hubert J. Farnsworth

Hawkmoon

  • friend
  • Senior Member
  • ***
  • Posts: 27,243
Re: Honeywell Thermostat issue - blinking red light of obscurity
« Reply #6 on: September 15, 2017, 11:50:48 PM »
Try replacing that coin battery. It may be the backup power source, and if you had a prolonged power outage it may have gotten run down.
- - - - - - - - - - - - -
100% Politically Incorrect by Design

BobR

  • Just a pup compared to a few old dogs here!
  • friend
  • Senior Member
  • ***
  • Posts: 7,266
Re: Honeywell Thermostat issue - blinking red light of obscurity
« Reply #7 on: September 16, 2017, 01:34:18 AM »
I guess you may have already seen this one in your searches.

https://www.youtube.com/watch?v=KcC9CpGblqU


bob

Regolith

  • friend
  • Senior Member
  • ***
  • Posts: 6,171
Re: Honeywell Thermostat issue - blinking red light of obscurity
« Reply #8 on: September 16, 2017, 02:12:17 AM »
Try replacing that coin battery. It may be the backup power source, and if you had a prolonged power outage it may have gotten run down.

I was thinking it could be something like that. Think I'll give this a try. Have to go into town tomorrow to get the battery, though.

I guess you may have already seen this one in your searches.

https://www.youtube.com/watch?v=KcC9CpGblqU

bob

Unfortunately, that's not exactly same model. Mine uses a coin battery instead of AAAs, and you have to pull the front faceplate of the unit off, remove the touch screen and circuit board from the housing, and THEN you can get to the coin battery, which is mounted on the back of the circuit board.
The price of freedom is eternal vigilance. - Thomas Jefferson

Necessity is the plea for every infringement of human freedom. It is the argument of tyrants; it is the creed of slaves. - William Pitt the Younger

Perfectly symmetrical violence never solved anything. - Professor Hubert J. Farnsworth

TechMan

  • Administrator
  • Senior Member
  • *****
  • Posts: 10,562
  • Yes, your moderation has been outsourced.
Re: Honeywell Thermostat issue - blinking red light of obscurity
« Reply #9 on: September 16, 2017, 06:39:12 AM »
Have you checked all your breakers and made sure none of them are tripped?
Quote
Hawkmoon - Never underestimate another person's capacity for stupidity. Any time you think someone can't possibly be that dumb ... they'll prove you wrong.

Bacon and Eggs - A day's work for a chicken; A lifetime commitment for a pig.
Stupidity will always be its own reward.
Bad decisions make good stories.

Quote
Viking - The problem with the modern world is that there aren't really any predators eating stupid people.

K Frame

  • friend
  • Senior Member
  • ***
  • Posts: 44,176
  • I Am Inimical
Re: Honeywell Thermostat issue - blinking red light of obscurity
« Reply #10 on: September 16, 2017, 07:01:07 AM »
I just found this...

http://www.hannabery.com/faq9.shtml

According to that, your outdoor unit might be in lockout mode.
Carbon Monoxide, sucking the life out of idiots, 'tards, and fools since man tamed fire.

Ben

  • Administrator
  • Senior Member
  • *****
  • Posts: 45,924
  • I'm an Extremist!
Re: Honeywell Thermostat issue - blinking red light of obscurity
« Reply #11 on: September 16, 2017, 10:37:20 AM »
Have you checked all your breakers and made sure none of them are tripped?

Related to that, do you have a remote thermometer that you can shoot up to one of your registers and get a temp reading? If so, does it seem warmer than normal (I'm assuming you're using AC this time of year)?

While I don't have a thermostat like yours, after power outages (or even brownouts) at both my house and my rentals, I have had the following happen several times: Unit turns on, but air comes out of the registers at around 70+ degrees instead of the high 50s.

My HVAC guy taught me a trick, because he runs into a lot of this. I forget which component he said is affected, but often after an outage something goes out of whack if the unit was running when the outage hit. The way he told me to fix it is to turn off the thermostat, shut off power at the breaker for 30 seconds than turn the breaker on again and turn on the thermostat. This has worked every time for me.

Kinda like "Have you tried turning it off and on again?"  :laugh:
"I'm a foolish old man that has been drawn into a wild goose chase by a harpy in trousers and a nincompoop."

never_retreat

  • Head Muckety Muck
  • friend
  • Senior Member
  • ***
  • Posts: 3,158
Re: Honeywell Thermostat issue - blinking red light of obscurity
« Reply #12 on: September 16, 2017, 12:23:21 PM »
The little transformer that makes the 24 volts. Can you check that?
I needed a mod to change my signature because the concept of "family friendly" eludes me.
Just noticed that a mod changed my signature. How long ago was that?
A few months-mods

Regolith

  • friend
  • Senior Member
  • ***
  • Posts: 6,171
Re: Honeywell Thermostat issue - blinking red light of obscurity
« Reply #13 on: September 16, 2017, 06:04:43 PM »
Have you checked all your breakers and made sure none of them are tripped?

Yes. One was tripped right after the power outage, but it wasn't related to the heat pump or thermostat.

I just found this...

http://www.hannabery.com/faq9.shtml

According to that, your outdoor unit might be in lockout mode.

Related to that, do you have a remote thermometer that you can shoot up to one of your registers and get a temp reading? If so, does it seem warmer than normal (I'm assuming you're using AC this time of year)?

While I don't have a thermostat like yours, after power outages (or even brownouts) at both my house and my rentals, I have had the following happen several times: Unit turns on, but air comes out of the registers at around 70+ degrees instead of the high 50s.

My HVAC guy taught me a trick, because he runs into a lot of this. I forget which component he said is affected, but often after an outage something goes out of whack if the unit was running when the outage hit. The way he told me to fix it is to turn off the thermostat, shut off power at the breaker for 30 seconds than turn the breaker on again and turn on the thermostat. This has worked every time for me.

Kinda like "Have you tried turning it off and on again?"  :laugh:

The  nothing's running, so there's nothing to check. But I think I'll try turning everything off and on again, per Mike's link.

The little transformer that makes the 24 volts. Can you check that?

I'm not sure what you're talking about, but if you can clarify I probably can.
The price of freedom is eternal vigilance. - Thomas Jefferson

Necessity is the plea for every infringement of human freedom. It is the argument of tyrants; it is the creed of slaves. - William Pitt the Younger

Perfectly symmetrical violence never solved anything. - Professor Hubert J. Farnsworth

Regolith

  • friend
  • Senior Member
  • ***
  • Posts: 6,171
Re: Honeywell Thermostat issue - blinking red light of obscurity
« Reply #14 on: September 16, 2017, 06:15:09 PM »
 Just turned everything off and then on again. No joy.  =(

Gonna try the battery next, I guess, soon as I have time to get to the store.
The price of freedom is eternal vigilance. - Thomas Jefferson

Necessity is the plea for every infringement of human freedom. It is the argument of tyrants; it is the creed of slaves. - William Pitt the Younger

Perfectly symmetrical violence never solved anything. - Professor Hubert J. Farnsworth

Scout26

  • I'm a leaf on the wind.
  • friend
  • Senior Member
  • ***
  • Posts: 25,997
  • I spent a week in that town one night....
Re: Honeywell Thermostat issue - blinking red light of obscurity
« Reply #15 on: September 16, 2017, 09:14:14 PM »
Are you sure you aren't missing 3 AA batteries ??
Some days even my lucky rocketship underpants won't help.


Bring me my Broadsword and a clear understanding.
Get up to the roundhouse on the cliff-top standing.
Take women and children and bed them down.
Bless with a hard heart those that stand with me.
Bless the women and children who firm our hands.
Put our backs to the north wind.
Hold fast by the river.
Sweet memories to drive us on,
for the motherland.

Regolith

  • friend
  • Senior Member
  • ***
  • Posts: 6,171
Re: Honeywell Thermostat issue - blinking red light of obscurity
« Reply #16 on: September 16, 2017, 10:47:59 PM »
Are you sure you aren't missing 3 AA batteries ??

No place to put them. :P


I replaced the coin battery about 10 minutes ago, and now everything is working, so it looks like that may have been the issue.